normal Mitsubishi VRF units to 1 CoolLinkNet

  • Andrew
  • Andrew's Avatar Topic Author
13 Dec 2016 11:44 #664 by Andrew
Good morning,

I was told that I could hook up 3 indoor Mitsubishi VRF units to 1
CoolLinkNet device. We have 5 indoor units, so we would need 2
CoolLinkNet devices.

Was I misinformed? Can I only connect one unit to the CoolLinkNet
device?

Thanks,

Best regards
More
13 Dec 2016 11:47 #665 by marcom
Replied by marcom on topic Mitsubishi VRF units to 1 CoolLinkNet
Dear Andrew,
Individual unit control - one by one (like thermostat) you need one coollink per unit.
If you want to control in a group - one coollink manages up to 16.
Best regards

Marcom S.r.l.