normal Multiple Mitsubishi Electric Bus

  • Anonimi
  • Anonimi's Avatar Topic Author
21 Mar 2017 08:59 #796 by Anonimi
Multiple Mitsubishi Electric Bus was created by Anonimi
We have a question about CoollMasterNet.

We have 3 mistubischi electric bus in a building. Customer asks us if it is possible to manage it with our Crestron processor; We saw the CoolMasterNet has 7 Lines input on board; but is it possibile to manage all of these buses togher on only one coolmasternet? or do we need more CoolMasterNet?

Where we need to connect it?

some additional information:

- Internal FCU is a PLFY-P25VFM-E1
- External unit are a PURY-P250 YLM-A1 and a PURY-P200 YLM-A1
More
21 Mar 2017 08:59 #797 by marcom
Replied by marcom on topic Multiple Mitsubishi Electric Bus
Actually, you can wire all 3 Mitsubishi systems in one bus, if there is not more than 50 indoor units.

You need to daisy chain them by Tb7 communication line.

In this case, you will only need one CoolMasterNet.
If not, you will need 2 CoolMasterNet units, + additional HVAC port license for one of them.