11 May 2017 14:45 #894 by Luke
Group units in Coolmasternet was created by Luke
Dear support
I'm using CoolMasterNet with SANYO
I have a problem

I have more units in a single room. But I have only one temperature probe in that room.
BTICINO driver isn’t able to split the temperature to 3 units in the same room

Is it possible to group units in the same room?
Thanks for feedback
More
11 May 2017 14:46 #895 by marcom
Replied by marcom on topic Group units in Coolmasternet
Good day,

First - I would suggest updating the newest firmware (attached). The procedure is here:
www.coolautomation.wiki/index.php?title=CoolMasterNet_FW_Update

You may group the 3 units, however you will e able to control all 3 by sending commands to the one (master).
If that is what you are expecting, please use PuTTY to connect to CoolMasterNet and to execute commands:
www.coolautomation.wiki/index.php?title=CoolMasterNet_FAQ

The command to group is (if you decide that the master is L1.101)
group L1.101 L1.102

group L1.101 L1.103

By sending a command 'on' to L1.101, L1.102 and L1.103 will turn on as well.

Thank you

Marcom S.r.l.