normal connect MAC-333IF-E to coolmasternet

  • Valerio
  • Avatar di Valerio Autore della discussione
02/05/2018 10:12 #1369 da Valerio
connect MAC-333IF-E to coolmasternet è stato creato da Valerio
Hello,
Can you please provide detail instructions how do we connect MAC-333IF-E to coolmasternet?

Thank you
Di più
02/05/2018 10:19 #1370 da marcom
Risposta da marcom al topic connect MAC-333IF-E to coolmasternet
Hello,

below you find the instructions to connect the MAC-333IF-E:

How to provide DC output on line L1

For Daikin or Mitsubishi Electric Non—VRV/VRF equipment, DC voltage supply by CoolMasterNet might be required for proper operation. Before enabling DC output from CoolMasterNet make sure there is no DC voltage on HVAC communication line. If no DC voltage detected: Daikin 14-16V DC, Mitsubishi 28-30V DC, do following:
  • Disconnect CoolMasterNet from power and HVAC line.
  • Change the dip switches S1 and S2 as shown below.
Daikin


Mitsubishi Electric

  • Turn ON the power for CoolMasterNet and connect it to HVAC line.
  • Issue below command:
and power reset CoolMasterNet.

Best regards

Marcom S.r.l.
via della Metallurgia, 11
37139 - Verona (VR)
Allegati:
  • ayham
  • Avatar di ayham Autore della discussione
24/07/2018 11:57 #1421 da ayham
Risposta da ayham al topic connect MAC-333IF-E to coolmasternet
I measured 15 volt on the M.Net bus so do I need extra power... where can I find S1 and S2....
Di più
24/07/2018 12:14 #1422 da marcom
Risposta da marcom al topic connect MAC-333IF-E to coolmasternet
Good Morning,

If there is voltage on the bus, DIP switches S1 and S2 must not be enabled.

Best Regards

Marcom S.r.l.
via della Metallurgia, 11
37139 - Verona (VR)