normal Suggestion for a Omron BACnet Gateway

  • Anonimi
  • Avatar di Anonimi Autore della discussione
18/07/2016 09:16 #429 da Anonimi
Suggestion for a Omron BACnet Gateway è stato creato da Anonimi
Dear all,

I have to let commercial BMS commnunicate with Omron PLC.
BMS supports different protocols but it is now usingmainly BACnet/IP.
Any suggestions?
Di più
18/07/2016 09:28 #430 da marcom
Risposta da marcom al topic Suggestion for a Omron BACnet Gateway
Dear customer,

we have a powerfull gateway in our catalogue to achive your task.
Gateway is from Protocessor, leader company in gateway for protocol conversion.

This gateway can read Omron FINS data and publish it as BACnet IP data.
It can also write to the Omron FINS devices.

In summary, this gateway can act as:
  • Client/Master on the BACnet IP network: Hence it is capable of reading data from the various BACnet slave devices and writing data to them if required.
  • Server/Slave on the BACnet IP network: You can use the gateway in this mode if you have a BACnet IP master on the network which would be reading data from the gateway.
  • Client/Master on the Omron FINS network: Hence it is capable of reading data from the various Omron FINS devices and writing data to them if required.
  • Server/Slave on the Omron FINS network: Various Omron FINS devices can read/write on the gateway.

We will configure the gateway for you based on your requirement and support you during commissioning of the gateway, so you do not have to worry about configuring the FieldServer gateway.

However, it is very helpful to know how to configure the devices. All the required tools and supporting product manuals with be provided completely free of cost with your purchase.

Configuration of the FieldServer is done using a '.csv' file. This file can be edited using any text editor

In this file we need to enter information for the Client and Server side interfaces of the FieldServer. This includes but is not limited to:
  • Node ids of the slave devices
  • IP addresses/device address of the slave devices
  • Baud rate, parity, stop bits for serial communication
  • Scan rates

And finally we need to create an internal mapping that would map each data value read on the client side to a data value on the server side.

Marcom S.r.l.
via della Metallurgia, 11
37139 - Verona (VR)
Powered by Forum Kunena
Avviso
  • I prezzi sul sito sono IVA esclusa.